1. Stepgen
This component provides software based generation of step pulses in response to position or velocity commands. In position mode, it has a built in pre-tuned position loop, so PID tuning is not required. In velocity mode, it drives a motor at the commanded speed, while obeying velocity and acceleration limits. It is a realtime component only, and depending on CPU speed, etc, is capable of maximum step rates of 10kHz to perhaps 50kHz. Figure [fig:Stepgen-Block-Diag] shows three block diagrams, each is a single step pulse generator. The first diagram is for step type 0, (step and direction). The second is for step type 1 (up/down, or pseudo-PWM), and the third is for step types 2 through 14 (various stepping patterns). The first two diagrams show position mode control, and the third one shows velocity mode. Control mode and step type are set independently, and any combination can be selected.
1.1. Installing
halcmd: loadrt stepgen step_type=<type-array> [ctrl_type=<ctrl_array>]
<type-array> is a series of comma separated decimal integers. Each number causes a single step pulse generator to be loaded, the value of the number determines the stepping type. <ctrl_array> is a comma separated series of p or v characters, to specify position or velocity mode. ctrl_type is optional, if ommitted, all of the step generators will be position mode.
For example:
halcmd: loadrt stepgen step_type=0,0,2 ctrl_type=p,p,v
will install three step generators. The first two use step type 0 (step and direction) and run in position mode. The last one uses step type 2 (quadrature) and runs in velocity mode. The default value for <config-array> is 0,0,0 which will install three type 0 (step/dir) generators. The maximum number of step generators is 8 (as defined by MAX_CHAN in stepgen.c). Each generator is independent, but all are updated by the same function(s) at the same time. In the following descriptions, <chan> is the number of a specific generator. The first generator is number 0.
1.2. Removing
halcmd: unloadrt stepgen
1.3. Pins
Each step pulse generator will have only some of these pins, depending on the step type and control type selected.
(float) stepgen.<chan>.position-cmd - Desired motor position, in position units (position mode only).
(float) stepgen.<chan>.velocity-cmd - Desired motor velocity, in position units per second (velocity mode only).
(s32) stepgen.<chan>.counts - Feedback position in counts, updated by capture_position().
(float) stepgen.<chan>.position-fb - Feedback position in position units, updated by capture_position().
(bit) stepgen.<chan>.enable - Enables output steps - when false, no steps are generated.
(bit) stepgen.<chan>.step - Step pulse output (step type 0 only).
(bit) stepgen.<chan>.dir - Direction output (step type 0 only).
(bit) stepgen.<chan>.up - UP pseudo-PWM output (step type 1 only).
(bit) stepgen.<chan>.down - DOWN pseudo-PWM output (step type 1 only).
(bit) stepgen.<chan>.phase-A - Phase A output (step types 2-14 only).
(bit) stepgen.<chan>.phase-B - Phase B output (step types 2-14 only).
(bit) stepgen.<chan>.phase-C - Phase C output (step types 3-14 only).
(bit) stepgen.<chan>.phase-D - Phase D output (step types 5-14 only).
(bit) stepgen.<chan>.phase-E - Phase E output (step types 11-14 only).
1.4. Parameters
(float) stepgen.<chan>.position-scale - Steps per position unit. This parameter is used for both output and feedback.
(float) stepgen.<chan>.maxvel - Maximum velocity, in position units per second. If 0.0, has no effect.
(float) stepgen.<chan>.maxaccel - Maximum accel/decel rate, in positions units per second squared. If 0.0, has no effect.
(float) stepgen.<chan>.frequency - The current step rate, in steps per second.
(float) stepgen.<chan>.steplen - Length of a step pulse (step type 0 and 1) or minimum time in a given state (step types 2-14), in nano-seconds.
(float) stepgen.<chan>.stepspace - Minimum spacing between two step pulses (step types 0 and 1 only), in nano-seconds.
(float) stepgen.<chan>.dirsetup - Minimum time from a direction change to the beginning of the next step pulse (step type 0 only), in nanoseconds.
(float) stepgen.<chan>.dirhold - Minmum time from the end of a step pulse to a direction change (step type 0 only), in nanoseconds.
(float) stepgen.<chan>.dirdelay - Minmum time any step to a step in the opposite direction (step types 1-14 only), in nano-seconds.
(s32) stepgen.<chan>.rawcounts - The raw feedback count, updated by make_pulses().
In position mode, the values of maxvel and maxaccel are used by the internal position loop to avoid generating step pulse trains that the motor cannot follow. When set to values that are appropriate for the motor, even a large instantaneous change in commanded position will result in a smooth trapezoidal move to the new location. The algorithm works by measuring both position error and velocity error, and calculating an acceleration that attempts to reduce both to zero at the same time. For more details, including the contents of the control equation box, consult the code.
In velocity mode, maxvel is a simple limit that is applied to the commanded velocity, and maxaccel is used to ramp the actual frequency if the commanded velocity changes abruptly. As in position mode, proper values for these parameters ensure that the motor can follow the generated pulse train.
1.5. Step Types
The step generator supports 15 different step types. Step type 0 is the most familiar, standard step and direction. When configured for step type 0, there are four extra parameters that determine the exact timing of the step and direction signals. See figure StepDir Timing for the meaning of these parameters. The parameters are in nanoseconds, but will be rounded up to an integer multiple of the thread period for the threaed that calls make_pulses(). For example, if make_pulses() is called every 16 us, and steplen is 20000, then the step pulses will be 2 x 16 = 32 us long. The default value for all four of the parameters is 1ns, but the automatic rounding takes effect the first time the code runs. Since one step requires steplen ns high and stepspace ns low, the maximum frequency is 1,000,000,000 divided by (steplen+stepspace). If maxfreq is set higher than that limit, it will be lowered automatically. If maxfreq is zero, it will remain zero, but the output frequency will still be limited.
Step type 1 has two outputs, up and down. Pulses appear on one or the other, depending on the direction of travel. Each pulse is steplen ns long, and the pulses are separated by at least stepspace ns. The maximum frequency is the same as for step type 0. If maxfreq is set higher than the limit it will be lowered. If maxfreq is zero, it will remain zero but the output frequency will still be limited.
Step types 2 through 14 are state based, and have from two to five outputs. On each step, a state counter is incremented or decremented. Figures [fig:Two-and-Three-Phase], [fig:Four-Phase], and [fig:Five-Phase] show the output patterns as a function of the state counter. The maximum frequency is 1,000,000,000 divided by steplen, and as in the other modes, maxfreq will be lowered if it is above the limit.
1.6. Functions
The component exports three functions. Each function acts on all of the step pulse generators - running different generators in different threads is not supported.
(funct) stepgen.make-pulses - High speed function to generate and count pulses (no floating point).
(funct) stepgen.update-freq - Low speed function does position to velocity conversion, scaling and limiting.
(funct) stepgen.capture-position - Low speed function for feedback, updates latches and scales position.
The high speed function stepgen.make-pulses should be run in a very fast thread, from 10 to 50 us depending on the capabilities of the computer. That thread’s period determines the maximum step frequency, since steplen, stepspace, dirsetup, dirhold, and dirdelay are all rounded up to a integer multiple of the thread periond in nanoseconds. The other two functions can be called at a much lower rate.
2. PWMgen
This component provides software based generation of PWM (Pulse Width Modulation) and PDM (Pulse Density Modulation) waveforms. It is a realtime component only, and depending on CPU speed, etc, is capable of PWM frequencies from a few hundred Hertz at pretty good resolution, to perhaps 10KHz with limited resolution.
2.1. Installing
loadrt pwmgen output_type=<config-array>
The <config-array> is a series of comma separated decimal integers. Each number causes a single PWM generator to be loaded, the value of the number determines the output type. The following example will install three PWM generators. There is no default value, if <config-array> is not specified, no PWM generators will be installed. The maximum number of frequency generators is 8 (as defined by MAX_CHAN in pwmgen.c). Each generator is independent, but all are updated by the same function(s) at the same time. In the following descriptions, <chan> is the number of a specific generator. The first generator is number 0.
loadrt pwmgen output_type=0,1,2
2.2. Removing
unloadrt pwmgen
2.3. Output Types
The PWM generator supports three different output types.
Output type 0 - PWM output pin only. Only positive commands are accepted, negative values are treated as zero (and will be affected by the parameter min-dc if it is non-zero).
Output type 1 - PWM/PDM and direction pins. Positive and negative inputs will be output as positive and negative PWM. The direction pin is false for positive commands, and true for negative commands. If your control needs positive PWM for both CW and CCW use the abs component to convert your PWM signal to positive value when a negative input is input.
Output type 2 - UP and DOWN pins. For positive commands, the PWM signal appears on the up output, and the down output remains false. For negative commands, the PWM signal appears on the down output, and the up output remains false. Output type 2 is suitable for driving most H-bridges.
2.4. Pins
Each PWM generator will have the following pins:
(float) pwmgen.<chan>.value - Command value, in arbitrary units. Will be scaled by the scale parameter (see below).
(bit) pwmgen.<chan>.enable - Enables or disables the PWM generator outputs.
Each PWM generator will also have some of these pins, depending on the output type selected:
(bit) pwmgen.<chan>.pwm - PWM (or PDM) output, (output types 0 and 1 only).
(bit) pwmgen.<chan>.dir - Direction output (output type 1 only).
(bit) pwmgen.<chan>.up - PWM/PDM output for positive input value (output type 2 only).
(bit) pwmgen.<chan>.down - PWM/PDM output for negative input value (output type 2 only).
2.5. Parameters
(float) pwmgen.<chan>.scale - Scaling factor to convert value from arbitrary units to duty cycle.
(float) pwmgen.<chan>.pwm-freq - Desired PWM frequency, in Hz. If 0.0, generates PDM instead of PWM. If set higher than internal limits, next call of update_freq() will set it to the internal limit. If non-zero, and dither is false, next call of update_freq() will set it to the nearest integer multiple of the make_pulses() function period.
(bit) pwmgen.<chan>.dither-pwm - If true, enables dithering to achieve average PWM frequencies or duty cycles that are unobtainable with pure PWM. If false, both the PWM frequency and the duty cycle will be rounded to values that can be achieved exactly.
(float) pwmgen.<chan>.min-dc - Minimum duty cycle, between 0.0 and 1.0 (duty cycle will go to zero when disabled, regardless of this setting).
(float) pwmgen.<chan>.max-dc - Maximum duty cycle, between 0.0 and 1.0.
(float) pwmgen.<chan>.curr-dc - Current duty cycle - after all limiting and rounding (read only).
2.6. Functions
The component exports two functions. Each function acts on all of the PWM generators - running different generators in different threads is not supported.
(funct) pwmgen.make-pulses - High speed function to generate PWM waveforms (no floating point).
(funct) pwmgen.update - Low speed function to scale and limit value and handle other parameters.
The high speed function pwmgen.make-pulses should be run in a very fast thread, from 10 to 50 us depending on the capabilities of the computer. That thread’s period determines the maximum PWM carrier frequency, as well as the resolution of the PWM or PDM signals. The other function can be called at a much lower rate.
3. Encoder
This component provides software based counting of signals from quadrature encoders. It is a realtime component only, and depending on CPU speed, latency, etc, is capable of maximum count rates of 10kHz to perhaps up to 50kHz. Figure [fig:Encoder-Block-Diag] is a block diagram of one channel of encoder counter.
3.1. Installing
halcmd: loadrt encoder [num_chan=<counters>]
<counters> is the number of encoder counters that you want to install. If numchan is not specified, three counters will be installed. The maximum number of counters is 8 (as defined by MAX_CHAN in encoder.c). Each counter is independent, but all are updated by the same function(s) at the same time. In the following descriptions, <chan> is the number of a specific counter. The first counter is number 0.
3.2. Removing
halcmd: unloadrt encoder
3.3. Pins
encoder.<chan>.counter-mode (bit, I/O) (default: FALSE) - Enables counter mode. When true, the counter counts each rising edge of the phase-A input, ignoring the value on phase-B. This is useful for counting the output of a single channel (non-quadrature) sensor. When false, it counts in quadrature mode.
encoder.<chan>.counts (s32, Out) - Position in encoder counts.
encoder.<chan>.counts-latched (s32, Out) - Not used at this time.
encoder.<chan>.index-enable (bit, I/O) - When True, counts and position are reset to zero on next rising edge of Phase Z. At the same time, index-enable is reset to zero to indicate that the rising edge has occoured. The index-enable pin is bi-directional. If index-enable is False, the Phase Z channel of the encoder will be ignored, and the counter will count normally. The encoder driver will never set index-enable True. However, some other component may do so.
encoder.<chan>.latch-falling (bit, In) (default: TRUE) - Not used at this time.
encoder.<chan>.latch-input (bit, In) (default: TRUE) - Not used at this time.
encoder.<chan>.latch-rising (bit, In) - Not used at this time.
encoder.<chan>.min-speed-estimate (float, in) - Determine the minimum true velocity magnitude at which velocity will be estimated as nonzero and postition-interpolated will be interpolated. The units of min-speed-estimate are the same as the units of velocity . Scale factor, in counts per length unit. Setting this parameter too low will cause it to take a long time for velocity to go to 0 after encoder pulses have stopped arriving.
encoder.<chan>.phase-A (bit, In) - Phase A of the quadrature encoder signal.
encoder.<chan>.phase-B (bit, In) - Phase B of the quadrature encoder signal.
encoder.<chan>.phase-Z (bit, In) - Phase Z (index pulse) of the quadrature encoder signal.
encoder.<chan>.position (float, Out) - Position in scaled units (see position-scale).
encoder.<chan>.position-interpolated (float, Out) - Position in scaled units, interpolated between encoder counts. The position-interpolated attempts to interpolate between encoder counts, based on the most recently measured velocity. Only valid when velocity is approximately constant and above min-speed-estimate. Do not use for position control, since its value is incorrect at low speeds, during direction reversals, and during speed changes. However, it allows a low ppr encoder (including a one pulse per revolution encoder) to be used for lathe threading, and may have other uses as well.
encoder.<chan>.position-latched (float, Out) - Not used at this time.
encoder.<chan>.position-scale (float, I/O) - Scale factor, in counts per length unit. For example, if position-scale is 500, then 1000 counts of the encoder will be reported as a position of 2.0 units.
encoder.<chan>.rawcounts (s32, In) - The raw count, as determined by update-counters. This value is updated more frequently than counts and position. It is also unaffected by reset or the index pulse.
encoder.<chan>.reset (bit, In) - When True, force counts and position to zero immediately.
encoder.<chan>.velocity (float, Out) - Velocity in scaled units per second. encoder uses an algorithm that greatly reduces quantization noise as compared to simply differentiating the position output. When the magnitude of the true velocity is below min-velocity-estimate, the velocity output is 0.
encoder.<chan>.x4-mode (bit, I/O) (default: TRUE) - Enables times-4 mode. When true, the counter counts each edge of the quadrature waveform (four counts per full cycle). When false, it only counts once per full cycle. In counter-mode, this parameter is ignored. The 1x mode is useful for some jogwheels.
3.4. Parameters
encoder.<chan>.capture-position.time (s32, RO)
encoder.<chan>.capture-position.tmax (s32, RW)
encoder.<chan>.update-counters.time (s32, RO)
encoder.<chan>.update-counter.tmax (s32, RW)
3.5. Functions
The component exports two functions. Each function acts on all of the encoder counters - running different counters in different threads is not supported.
(funct) encoder.update-counters - High speed function to count pulses (no floating point).
(funct) encoder.capture-position - Low speed function to update latches and scale position.
4. PID
This component provides Proportional/Integral/Derivative control loops. It is a realtime component only. For simplicity, this discussion assumes that we are talking about position loops, however this component can be used to implement other feedback loops such as speed, torch height, temperature, etc. Figure [fig:PID-block-diag] is a block diagram of a single PID loop.
4.1. Installing
halcmd: loadrt pid [num_chan=<loops>] [debug=1]
<loops> is the number of PID loops that you want to install. If numchan is not specified, one loop will be installed. The maximum number of loops is 16 (as defined by MAX_CHAN in pid.c). Each loop is completely independent. In the following descriptions, <loopnum> is the loop number of a specific loop. The first loop is number 0.
If debug=1 is specified, the component will export a few extra parameters that may be useful during debugging and tuning. By default, the extra parameters are not exported, to save shared memory space and avoid cluttering the parameter list.
4.2. Removing
halcmd: unloadrt pid
4.3. Pins
The three most important pins are
(float) pid.<loopnum>.command - The desired position, as commanded by another system component.
(float) pid.<loopnum>.feedback - The present position, as measured by a feedback device such as an encoder.
(float) pid.<loopnum>.output - A velocity command that attempts to move from the present position to the desired position.
For a position loop, command and feedback are in position units. For a linear axis, this could be inches, mm, meters, or whatever is relevant. Likewise, for an angular axis, it could be degrees, radians, etc. The units of the output pin represent the change needed to make the feedback match the command. As such, for a position loop Output is a velocity, in inches/sec, mm/sec, degrees/sec, etc. Time units are always seconds, and the velocity units match the position units. If command and feedback are in meters, then output is in meters per second.
Each loop has two pins which are used to monitor or control the general operation of the component.
(float) pid.<loopnum>.error - Equals .command minus .feedback.
(bit) pid.<loopnum>.enable - A bit that enables the loop. If .enable is false, all integrators are reset, and the output is forced to zero. If .enable is true, the loop operates normally.
Pins used to report saturation. Saturation occurs when the output of the PID block is at its maximum or minimum limit.
(bit) pid.<loopnum>.saturated - True when output is saturated.
(float) pid.<loopnum>.saturated_s - The time the output has been saturated.
(s32) pid.<loopnum>.saturated_count - The time the output has been saturated.
4.4. Parameters
The PID gains, limits, and other tunable features of the loop are implemented as parameters.
(float) pid.<loopnum>.Pgain - Proportional gain
(float) pid.<loopnum>.Igain - Integral gain
(float) pid.<loopnum>.Dgain - Derivative gain
(float) pid.<loopnum>.bias - Constant offset on output
(float) pid.<loopnum>.FF0 - Zeroth order feedforward - output proportional to command (position).
(float) pid.<loopnum>.FF1 - First order feedforward - output proportional to derivative of command (velocity).
(float) pid.<loopnum>.FF2 - Second order feedforward - output proportional to 2nd derivative of command (acceleration)
[FF2 is not currently implemented, but it will be added. Consider this note a “FIXME” for the code]
(float) pid.<loopnum>.deadband - Amount of error that will be ignored
(float) pid.<loopnum>.maxerror - Limit on error
(float) pid.<loopnum>.maxerrorI - Limit on error integrator
(float) pid.<loopnum>.maxerrorD - Limit on error derivative
(float) pid.<loopnum>.maxcmdD - Limit on command derivative
(float) pid.<loopnum>.maxcmdDD - Limit on command 2nd derivative
(float) pid.<loopnum>.maxoutput - Limit on output value
All of the max limits are implemented such that if the parameter value is zero, there is no limit.
If debug=1 was specified when the component was installed, four additional parameters will be exported:
(float) pid.<loopnum>.errorI - Integral of error.
(float) pid.<loopnum>.errorD - Derivative of error.
(float) pid.<loopnum>.commandD - Derivative of the command.
(float) pid.<loopnum>.commandDD - 2nd derivative of the command.
4.5. Functions
The component exports one function for each PID loop. This function performs all the calculations needed for the loop. Since each loop has its own function, individual loops can be included in different threads and execute at different rates.
(funct) pid.<loopnum>.do_pid_calcs - Performs all calculations for a single PID loop.
If you want to understand the exact algorithm used to compute the output of the PID loop, refer to figure [fig:PID-block-diag], the comments at the beginning of emc2/src/hal/components/pid.c , and of course to the code itself. The loop calculations are in the C function calc_pid().
5. Simulated Encoder
The simulated encoder is exactly that. It produces quadrature pulses with an index pulse, at a speed controlled by a HAL pin. Mostly useful for testing.
5.1. Installing
halcmd: loadrt sim-encoder num_chan=<number>
<number> is the number of encoders that you want to simulate. If not specified, one encoder will be installed. The maximum number is 8 (as defined by MAX_CHAN in sim_encoder.c).
5.2. Removing
halcmd: unloadrt sim-encoder
5.3. Pins
(float) sim-encoder.<chan-num>.speed - The speed command for the simulated shaft.
(bit) sim-encoder.<chan-num>.phase-A - Quadrature output.
(bit) sim-encoder.<chan-num>.phase-B - Quadrature output.
(bit) sim-encoder.<chan-num>.phase-Z - Index pulse output.
When .speed is positive, .phase-A leads .phase-B.
5.4. Parameters
(u32) sim-encoder.<chan-num>.ppr - Pulses Per Revolution.
(float) sim-encoder.<chan-num>.scale - Scale Factor for speed. The default is 1.0, which means that speed is in revolutions per second. Change to 60 for RPM, to 360 for degrees per second, 6.283185 for radians per seconed, etc.
Note that pulses per revolution is not the same as counts per revolution. A pulse is a complete quadrature cycle. Most encoder counters will count four times during one complete cycle.
5.5. Functions
The component exports two functions. Each function affects all simulated encoders.
(funct) sim-encoder.make-pulses - High speed function to generate quadrature pulses (no floating point).
(funct) sim-encoder.update-speed - Low speed function to read speed, do scaling, and set up make-pulses.
6. Debounce
Debounce is a realtime component that can filter the glitches created by mechanical switch contacts. It may also be useful in other applications where short pulses are to be rejected.
6.1. Installing
halcmd: loadrt debounce cfg=<config-string>
<config-string> is a series of comma separated decimal integers. Each number installs a group of identical debounce filters, the number determines how many filters are in the group.
For example:
halcmd: loadrt debounce cfg=1,4,2
will install three groups of filters. Group 0 contains one filter, group 1 contains four, and group 2 contains two filters. The default value for <config-string> is "1" which will install a single group containing a single filter. The maximum number of groups 8 (as defined by MAX_GROUPS in debounce.c). The maximum number of filters in a group is limited only by shared memory space. Each group is completely independent. All filters in a single group are identical, and they are all updated by the same function at the same time. In the following descriptions, <G> is the group number and <F> is the filter number within the group. The first filter is group 0, filter 0.
6.2. Removing
halcmd: unloadrt debounce
6.3. Pins
Each individual filter has two pins.
(bit) debounce.<G>.<F>.in - Input of filter <F> in group <G>.
(bit) debounce.<G>.<F>.out - Output of filter <F> in group <G>.
6.4. Parameters
Each group of filters has one parameter
[Each individual
filter also has an internal state variable. There is a
compile time switch that can export that variable as a parameter. This
is intended for testing, and simply wastes shared memory under normal
circumstances.]
(s32) debounce.<G>.delay - Filter delay for all filters in group <G>.
The filter delay is in units of thread periods. The minimum delay is zero. The output of a zero delay filter exactly follows its input - it doesn’t filter anything. As delay increases, longer and longer glitches are rejected. If delay is 4, all glitches less than or equal to four thread periods will be rejected.
6.5. Functions
Each group of filters has one function, which updates all the filters in that group simultaneously. Different groups of filters can be updated from different threads at different periods.
(funct) debounce.<G> - Updates all filters in group <G>.
7. Siggen
Siggen is a realtime component that generates square, triangle, and sine waves. It is primarily used for testing.
7.1. Installing
halcmd: loadrt siggen [num_chan=<chans>]
<chans> is the number of signal generators that you want to install. If numchan is not specified, one signal generator will be installed. The maximum number of generators is 16 (as defined by MAX_CHAN in siggen.c). Each generator is completely independent. In the following descriptions, <chan> is the number of a specific signal generator (the numbers start at 0).
7.2. Removing
halcmd: unloadrt siggen
7.3. Pins
Each generator has five output pins.
(float) siggen.<chan>.sine - Sine wave output.
(float) siggen.<chan>.cosine - Cosine output.
(float) siggen.<chan>.sawtooth - Sawtooth output.
(float) siggen.<chan>.triangle - Triangle wave output.
(float) siggen.<chan>.square - Square wave output.
All five outputs have the same frequency, amplitude, and offset.
In addition to the output pins, there are three control pins:
(float) siggen.<chan>.frequency - Sets the frequency in Hertz, default value is 1 Hz.
(float) siggen.<chan>.amplitude - Sets the peak amplitude of the output waveforms, default is 1.
(float) siggen.<chan>.offset - Sets DC offset of the output waveforms, default is 0.
For example, if siggen.0.amplitude is 1.0 and siggen.0.offset is 0.0, the outputs will swing from -1.0 to +1.0. If siggen.0.amplitude is 2.5 and siggen.0.offset is 10.0, then the outputs will swing from 7.5 to 12.5.
7.4. Parameters
None.
[Prior to version 2.1, frequency, amplitude, and offset
were parameters. They were changed to pins to allow control by other
components.]
7.5. Functions
(funct) siggen.<chan>.update - Calculates new values for all five outputs.
