1. Conventions
Conventions used in this section
In the G code prototypes the hyphen (-) stands for a real value and (<>) denotes an optional item.
If L- is written in a prototype the - will often be referred to as the L number, and so on for any other letter.
In the G code prototypes the word axes stands for any axis as defined in your configuration.
An optional value will be written like this <L->.
A real value may be:
  • An explicit number, 4
  • An expression, [2+2]
  • A parameter value, #88
  • A unary function value, acos[0]
In most cases, if axis words are given (any or all of X Y Z A B C U V W), they specify a destination point.
Axis numbers are in the currently active coordinate system, unless explicitly described as being in the absolute coordinate system.
Where axis words are optional, any omitted axes will retain their original value.
Any items in the G code prototypes not explicitly described as optional are required.
The values following letters are often given as explicit numbers. Unless stated otherwise, the explicit numbers can be real values. For example, G10 L2 could equally well be written G[2*5] L[1+1]. If the value of parameter 100 were 2, G10 L#100 would also mean the same.
2. G Code Quick Reference Table
Code Description
G0
Coordinated Straight Motion Rapid
G1
Coordinated Straight Motion Feed Rate
G2
Coordinated Helical Motion Feed Rate
G4
Dwell
G5.1
Quadratic B-Spline
G5.2
NURBs Block
G7
Diameter Mode (lathe)
G8
Radius Mode (lathe)
G10 L1
Set Tool Table Entry
G10 L10
Set Tool Table, Calculated, Workpiece
G10 L11
Set Tool Table, Calculated, Fixture
G10 L2
Coordinate System Origin Setting
G10 L20
Coordinate System Origin Setting Calculated
G17 - G19.1
Plane Select
G20
Units of Measure
G28 - G28.1
Go to Predefined Position
G30 - G30.1
G33
Spindle Synchronized Motion
G33.1
Rigid Tapping
G38.2 - G38.5
Probing
G40
Cancel Cutter Compensation
G41
Cutter Compensation
G41.1
Cutter Compensation Transient
G43
Use Tool Length Offset from Tool Table
G49
Cancel Tool Length Offset
G53
Motion in Machine Coordinate System
G54-G59
Select Coordinate System (1 - 6)
G59.1-G59.3
Select Coordinate System (7 - 9)
G61
Path Control Mode
G64
Path Control Mode with Optional Tolerance
G73
Drilling Cycle with Chip Breaking
G76
Multi-pass Threading Cycle (Lathe)
G80
Cancel Motion Modes
G81
Drilling Cycle
G82
Drilling Cycle with Dwell
G83
Drilling Cycle with Peck
G84
Right Hand Tapping Cycle (unimplemented)
G85
Boring Cycle, No Dwell, Feed Out
G86
Boring Cycle, Stop, Rapid Out
G87
Back-Boring Cycle (unimplemented)
G88
Boring Cycle, Stop, Manual Out (unimplemented)
G89
Boring Cycle, Dwell, Feed Out
G90
Distance Mode
G90.1
Arc Distance Mode
G92
Offset Coordinate Systems & Set Parameters
G92.1 G92.2
Cancel Offsets
G92.3
Apply Parameters to Offset Coordinate Systems
G93
Feed Modes
G96
Constant Surface Speed
G97
RPM Mode
G98
Canned Cycle Z Retract Mode
3. G0 Rapid Motion
G0 axes
For rapid linear (straight line) motion, program G0 'axes', where all the axis words are optional. The G0 is optional if the current motion mode is G0. This will produce coordinated linear motion to the destination point at the current maximum traverse rate (or slower if the machine will not go that fast). It is expected that cutting will not take place when a G0 command is executing.
G0 Example
G90 (set absolute distance mode)
G0 X1 Y-2.3 (Rapid linear move from current location to X1 Y-2.3)
M2 (end program)
  • See G90 & M2 sections for more information.
If cutter radius compensation is active, the motion will differ from the above; see the Radius Compensation Section.
If G53 is programmed on the same line, the motion will also differ; see the G53 Section for more information.
It is an error if:
  • An axis letter is without a real value.
  • An axis letter is used that is not configured
4. G1 Linear Feed
G1 axes
For linear (straight line) motion at programed feed rate (for cutting or not), program G1 'axes', where all the axis words are optional. The G1 is optional if the current motion mode is G1. This will produce coordinated linear motion to the destination point at the current feed rate (or slower if the machine will not go that fast).
G1 Example
G1 X1.2 Y-3 F10 (linear move at a feed rate of 10 from current position to X1.2 Y-3)
Z-2.3 (linear move at same feed rate from current position to Z-2.3)
Z1 F25 (linear move at a feed rate of 25 from current position to Z1)
M2 (end program)
  • See G90 & F & M2 sections for more information.
It is an error if:
  • No feed rate has been set.
5. G2, G3 Arc Feed
G2 or G3 axes offsets (center format)
G2 or G3 axes R- (radius format)
G2 or G3 offsets <P-> (full circles)
A circular or helical arc is specified using either G2 (clockwise arc) or G3 (counterclockwise arc). The direction (CW, CCW) is as viewed from the positive end of the axis about which the circular motion occurs.
The axis of the circle or helix must be parallel to the X, Y, or Z axis of the machine coordinate system. The axis (or, equivalently, the plane perpendicular to the axis) is selected with G17 (Z-axis, XY-plane), G18 (Y-axis, XZ-plane), or G19 (X-axis, YZ-plane). Planes 17.1, 18.1, and 19.1 are not currently supported. If the arc is circular, it lies in a plane parallel to the selected plane.
To program a helix, include the axis word perpendicular to the arc plane: for example, if in the G17 plane, include a Z word. This will cause the Z axis to move to the programmed value during the circular XY motion.
To program an arc that gives more than one full turn, use a P word specifying the number of full or partial turns of arc. If P is unspecified, the behavior is as if P1 was given: that is, only one full or partial turn will result, giving an arc less than or equal to one full circle. For example, if an arc is programmed with P2, the resulting motion will be more than one full circle and up to two full circles (depending on the programmed endpoint.) Multi turn helical arcs are supported and give motion useful for milling holes or threads.
If a line of code makes an arc and includes rotary axis motion, the rotary axes turn at a constant rate so that the rotary motion starts and finishes when the XYZ motion starts and finishes. Lines of this sort are hardly ever programmed.
The arc offset is relative or absolute as set by G90.1 & G91.1.
Two formats are allowed for specifying an arc: Center Format and Radius Format.
It is an error if:
5.1. Center Format Arcs
Center format arcs are more accurate than radius format arcs and are the preferred format to use.
The end point of the arc along with the offset to the center of the arc from the current location are used to program arcs that are less than a full circle. It is OK if the end point of the arc is the same as the current location.
The offset to the center of the arc from the current location and optionally the number of turns are used to program full circles.
When programming arcs an error due to rounding can result from using a precision of less than 4 decimal places (0.0000) for inch and less than 3 decimal places (0.000) for millimeters.
Incremental Arc Distance Mode
Arc center offsets are a relative distance from the start location of the arc. Incremental Arc Distance Mode is default.
One or more axis words and one or more offsets must be programmed for an arc that is less than 360 degrees.
No axis words and one or more offsets must be programmed for full circles. The P word defaults to 1 and is optional.
For more information on 'Incremental Arc Distance Mode see the G91.1 section.
Absolute Arc Distance Mode
Arc center offsets are the absolute distance from the current 0 position of the axis.
One or more axis words and both offsets must be programmed for arcs less than 360 degrees.
No axis words and both offsets must be programmed for full circles. The P word defaults to 1 and is optional.
For more information on 'Absolute Arc Distance Mode see the G90.1 section.
XY-plane (G17)
G2 or G3 <X- Y- Z- I- J- P->
  • Z - helix
  • I - X offset
  • J - Y offset
  • P - number of turns
XZ-plane (G18)
G2 or G3 <X- Z- Y- I- K- P->
  • Y - helix
  • I - X offset
  • K - Z offset
YZ-plane (G19)
G2 or G3 <Y- Z- X- J- K- P->
  • X - helix
  • J - Y offset
  • K - Z offset
It is an error if:
  • No feed rate is set with the F word.
  • No offsets are programmed.
  • When the arc is projected on the selected plane, the distance from the current point to the center differs from the distance from the end point to the center by more than (.05 inch/.5 mm) OR ((.0005 inch/.005mm) AND .1% of radius).
Deciphering the Error message Radius to end of arc differs from radius to start:
  • start - the current position
  • center - the center position as calculated using the i,j or k words
  • end - the programmed end point
  • r1 - radius from the start position to the center
  • r2 - radius from the end position to the center
5.2. Center Format Examples
Calculating arcs by hand can be difficult at times. One option is to draw the arc with a cad program to get the coordinates and offsets. Keep in mind the tolerance mentioned above, you may have to change the precision of your cad program to get the desired results. Another option is to calculate the coordinates and offset using formulas. As you can see in the following figures a triangle can be formed from the current position the end position and the arc center.
In the following figure you can see the start position is X0 Y0, the end position is X1 Y1. The arc center position is at X1 Y0. This gives us an offset from the start position of 1 in the X axis and 0 in the Y axis. In this case only an I offset is needed.
G2 Example Line
G2 X1 Y1 I1 F10 (clockwise arc in the XY plane)
images/g2.png
Figure 1. G2 Example
In the next example we see the difference between the offsets for Y if we are doing a G2 or a G3 move. For the G2 move the start position is X0 Y0, for the G3 move it is X0 Y1. The arc center is at X1 Y0.5 for both moves. The G2 move the J offset is 0.5 and the G3 move the J offset is -0.5.
G2-G3 Example Line
G2 X0 Y1 I1 J0.5 F25 (clockwise arc in the XY plane)
G3 X0 Y0 I1 J-0.5 F25 (counterclockwise arc in the XY plane)
images/g2-3.png
Figure 2. G2-G3 Example
G2 Example Line
G17 G2 X10 Y16 I3 J4 Z9 (helix arc with Z added)
The above example line will make a clockwise (as viewed from the positive Z-axis) circular or helical arc whose axis is parallel to the Z-axis, ending where X=10, Y=16, and Z=9, with its center offset in the X direction by 3 units from the current X location and offset in the Y direction by 4 units from the current Y location. If the current location has X=7, Y=7 at the outset, the center will be at X=10, Y=11. If the starting value of Z is 9, this is a circular arc; otherwise it is a helical arc. The radius of this arc would be 5.
In the center format, the radius of the arc is not specified, but it may be found easily as the distance from the center of the circle to either the current point or the end point of the arc.
5.3. Radius Format Arcs
G2 or G3 axes R-
  • R - radius from current position
It is not good practice to program radius format arcs that are nearly full circles or nearly semicircles because a small change in the location of the end point will produce a much larger change in the location of the center of the circle (and, hence, the middle of the arc). The magnification effect is large enough that rounding error in a number can produce out-of-tolerance cuts. For instance, a 1% displacement of the endpoint of a 180 degree arc produced a 7% displacement of the point 90 degrees along the arc. Nearly full circles are even worse. Other size arcs (in the range tiny to 165 degrees or 195 to 345 degrees) are OK.
In the radius format, the coordinates of the end point of the arc in the selected plane are specified along with the radius of the arc. Program G2 axes R- (or use G3 instead of G2 ). R is the radius. The axis words are all optional except that at least one of the two words for the axes in the selected plane must be used. The R number is the radius. A positive radius indicates that the arc turns through less than 180 degrees, while a negative radius indicates a turn of more than 180 degrees. If the arc is helical, the value of the end point of the arc on the coordinate axis parallel to the axis of the helix is also specified.
It is an error if:
  • both of the axis words for the axes of the selected plane are omitted
  • the end point of the arc is the same as the current point.
G2 Example Line
G17 G2 X10 Y15 R20 Z5 (radius format with arc)
The above example makes a clockwise (as viewed from the positive Z-axis) circular or helical arc whose axis is parallel to the Z-axis, ending where X=10, Y=15, and Z=5, with a radius of 20. If the starting value of Z is 5, this is an arc of a circle parallel to the XY-plane; otherwise it is a helical arc.
6. G4 Dwell
G4 P-
  • P - seconds to dwell
The P number is the time in seconds that all axes will remain unmoving. This does not affect spindle, coolant and other I/O.
G4 Example Line
G4 P1.5 (wait for 1.5 seconds before proceeding)
It is an error if:
  • the P number is negative.
7. G5.1 Quadratic B-spline
G5.1 X- Y- I- J-
  • I - X axis offset
  • J - Y axis offset
G5.1 creates a quadratic B-spline in the XY plane with the X and Y axis only. The offsets are I for X axis and J for Y axis.
It is an error if:
  • I and J offset is not specified
  • An axis other than X or Y is specified
  • The active plane is not G17
8. G5.2 G5.3 NURBs Block
G5.2 X- Y- P- <L->
X- Y- P- <L->
G5.3
Warning: G5.2, G5.3 is experimental and not fully tested.
G5.2 is for opening the data block defining a NURBs and G5.3 for closing the data block. In the lines between these two codes the curve control points are defined with both their related weights (P) and their parameter (L) which determines the order of the curve (k) and subsequently its degree (k-1).
Using this curve definition the knots of the NURBs curve are not defined by the user they are calculated by the inside algorithm, in the same way as it happens in a great number of graphic applications, where the curve shape can be modified only acting on either control points or weights.
G5.2 Example
G0 X0 Y0 (rapid move)
F10 (set feed rate)
G5.2 X0 Y1 P1 L3
     X2 Y2 P1
     X2 Y0 P1
     X0 Y0 P2
G5.3
; The rapid moves show the same path without the NURBs Block
G0 X0 Y1
   X2 Y2
   X2 Y0
   X0 Y0
M2
Sample NURBs Output
images/nurbs01.png
More information on NURBs can be found here:
9. G7 Lathe Diameter Mode
G7
Program G7 to enter the diameter mode for axis X on a lathe. When in the diameter mode the X axis moves on a lathe will be 1/2 the distance to the center of the lathe. For example X1 would move the cutter to 0.500” from the center of the lathe thus giving a 1” diameter part.
10. G8 Lathe Radius Mode
G8
Program G8 to enter the radius mode for axis X on a lathe. When in Radius mode the X axis moves on a lathe will be the distance from the center. Thus a cut at X1 would result in a part that is 2" in diameter. G8 is default at power up.
11. G10 L1 Set Tool Table
G10 L1 P- axes <R- I- J- Q->
  • P - tool number
  • R - radius of tool
  • I - front angle (lathe)
  • J - back angle (lathe)
  • Q - orientation (lathe)
G10 L1 sets the tool table for the P tool number to the values of the words.
A valid G10 L1 rewrites and reloads the tool table.
G10 L1 Example Line
G10 L1 P1 Z1.5 (set tool 1 Z offset from the machine origin to 1.5)
G10 L1 P2 R0.015 Q3 (lathe example setting tool 2 radius to 0.015 and orientation to 3)
It is an error if:
  • Cutter Compensation is on
  • The P number is unspecified
  • The P number is not a valid tool number from the tool table
For more information on cutter orientation used by the Q word, see the Lathe Tool Orientation diagram.
12. G10 L2 Set Coordinate System
G10 L2 P- <axes R->
  • P - coordinate system (0-9)
  • R - rotation about the Z axis
G10 L2 sets the origin of a coordinate system.
To specify a coordinate system program P1 to P9 corresponding to G54 to G59.3. For the currently active coordinate system program P0.
Optionally program R to indicate the rotation of the XY axis around the Z axis. All axis words are optional.
The origin of the coordinate system specified by the P number is set to the given values (in terms of the not offset machine coordinate system). Only those coordinates for which an axis word is included on the line will be set.
Being in incremental distance mode (G91) has no effect on G10 L2. The direction of rotation is CCW as viewed from the Top View.
Important Concepts:
  • G10 L2 Pn does not change from the current coordinate system to the one specified by P, you have to use G54-59.3 to select a coordinate system.
  • When a rotation is in effect jogging an axis will only move that axis in a positive or negative direction and not along the rotated axis.
  • If a G92 origin offset was in effect before G10 L2, it will continue to be in effect afterwards.
  • The coordinate system whose origin is set by a G10 command may be active or inactive at the time the G10 is executed. If it is currently active, the new coordinates take effect immediately.
It is an error if:
  • The P number does not evaluate to an integer in the range 0 to 9.
  • An axis is programmed that is not defined in the configuration.
G10 L2 Example Line
G10 L2 P1 X3.5 Y17.2
In the above example the origin of the first coordinate system (the one selected by G54) is set to be X=3.5 and Y=17.2. Because only X and Y are specified, the origin point is only moved in X and Y; the other coordinates are not changed.
G2 L2 Example Line
G10 L2 P1 X0 Y0 Z0 (clear offsets for X,Y & Z axes in coordinate system 1)
The above example sets the XYZ coordinates of the coordinate system 1 to the machine origin.
Table 1. Coordinate System
P Value Coordinate System G code
0
Active
n/a
1
1
G54
2
2
G55
3
3
G56
4
4
G57
5
5
G58
6
6
G59
7
7
G59.1
8
8
G59.2
9
9
G59.3
The coordinate system is described in the Coordinate System Section.
13. G10 L10 Set Tool Table
G10 L10 P- axes <R- I- J- Q->
  • P - tool number
G10 L10 changes the tool table entry for tool P so that if the tool offset is reloaded, with the machine in its current position and with the current G5x and G92 offsets active, the current coordinates for the given axes will become the given values. The axes that are not specified in the G10 L10 command will not be changed. This could be useful with a probe move as described in the G38 section.
G10 L10 Example
T1 M6 G43 (load tool 1 and tool length offsets)
G10 L10 P1 Z1.5 (set the current position for Z to be 1.5)
G43 (reload the tool length offsets from the changed tool table)
M2 (end program)
  • See T & M6 & G43 sections for more information.
It is an error if:
14. G10 L11 Set Tool Table
G10 L11 P- axes <R- I- J- Q->
G10 L11 is just like G10 L10 except that instead of setting the entry according to the current offsets, it is set so that the current coordinates would become the given value if the new tool offset is reloaded and the machine is placed in the G59.3 coordinate system without any G92 offset active.
This allows the user to set the G59.3 coordinate system according to a fixed point on the machine, and then use that fixture to measure tools without regard to other currently-active offsets.
It is an error if:
15. G10 L20 Set Coordinate System
G10 L20 P- axes <R->
G10 L20 is similar to G10 L2 except that instead of setting the offset/entry to the given value, it is set to a calculated value that makes the current coordinates become the given value.
G10 L20 Example Line
G10 L20 P1 X1.5 (set the X axis current location in coordinate system 1 to 1.5)
It is an error if:
16. G17 - G19.1 Plane Selection
These codes set the current plane as follows:
  • G17 - XY (default)
  • G18 - ZX
  • G19 - YZ
  • G17.1 - UV
  • G18.1 - WU
  • G19.1 - VW
The UV, WU and VW planes do not support arcs.
It is a good idea to include a plane selection in the preamble of each G code file.
The effects of having a plane selected are discussed in Section G2 G3 and Section G81 G89
17. G20, G21 Units
  • G20 - to use inches for length units.
  • G21 - to use millimeters for length units.
It is a good idea to include units in the preamble of each G code file.
18. G28, G28.1 Go to Predefined Position
  • G28 - makes a rapid traverse move from the current position to the absolute position of the values in parameters 5161-5166. The parameter values are in terms of the absolute coordinate system and the machine’s native coordinate system.
  • G28 axes - will make a rapid traverse move to the position specified by axes, then will make a rapid traverse move to the absolute position of the values in parameters 5161-5166.
  • G28.1 - stores the current absolute position into parameters 5161-5166.
G30 Example Line
G28 Z2.5 (rapid to Z2.5 then to location specified in the G28 stored parameters)
It is an error if :
  • Radius compensation is turned on
19. G30, G30.1 Go to Predefined Position
  • G30 - makes a rapid traverse move from the current position to the absolute position of the values in parameters 5181-5186. The parameter values are in terms of the absolute coordinate system and the machine’s native coordinate system.
  • G30 axes - will make a rapid traverse move to the position specified by axes, then will make a rapid traverse move to the absolute position of the values in parameters 5181-5186.
  • G30.1 - stores the current absolute position into parameters 5181-5186.
Note
G30 parameters will be used to move the tool when a M6 is programmed if [TOOL_CHANGE_AT_G30]=1 is in the [EMCIO] section of the ini file.
G30 Example Line
G30 Z2.5 (rapid to Z2.5 then to the location specified in the G30 stored parameters)
It is an error if :
20. G33 Spindle Synchronized Motion
G33 X- Y- Z- K-
  • K - distance per revolution
For spindle-synchronized motion in one direction, code G33 X- Y- Z- K- where K gives the distance moved in XYZ for each revolution of the spindle. For instance, if starting at Z=0, G33 Z-1 K.0625 produces a 1 inch motion in Z over 16 revolutions of the spindle. This command might be part of a program to produce a 16TPI thread. Another example in metric, G33 Z-15 K1.5 produces a movement of 15mm while the spindle rotates 10 times for a thread of 1.5mm.
Note
K follows the drive line described by X- Y- Z- and is not parallel to the Z axis.
Spindle-synchronized motions wait for spindle index, so multiple passes line up. G33 moves end at the programmed endpoint. G33 could be used to cut tapered threads or a fusee.
All the axis words are optional, except that at least one must be used.
G33 Example
G90 (absolute distance mode)
G0 X1 Z0.1 (rapid to position)
S100 M3 (start spindle turning)
G33 Z-2 K0.125 (move Z axis to -2 at a rate to equal 0.125 per revolution)
G0 X1.25 (rapid move tool away from work)
Z0.1 (rapid move to starting Z position)
M2 (end program)
  • See G90 & G0 & M2 sections for more information.
It is an error if:
  • All axis words are omitted.
  • The spindle is not turning when this command is executed
  • The requested linear motion exceeds machine velocity limits due to the spindle speed
21. G33.1 Rigid Tapping
G33.1 X- Y- Z- K-
For rigid tapping (spindle synchronized motion with return), code G33.1 X- Y- Z- K- where K- gives the distance moved for each revolution of the spindle. A rigid tapping move consists of the following sequence:
Warning
If the X Y coordinates specified are not the current coordinates when calling G33.1 for tapping the move will not be along the Z axis but will traverse from the current location to the X Y specified.
  1. A move to the specified coordinate, synchronized with the spindle at the given ratio and starting with a spindle index pulse.
  2. When reaching the endpoint, a command to reverse the spindle (e.g., from clockwise to counterclockwise).
  3. Continued synchronized motion beyond the specified end coordinate until the spindle actually stops and reverses.
  4. Continued synchronized motion back to the original coordinate.
  5. When reaching the original coordinate, a command to reverse the spindle a second time (e.g., from counterclockwise to clockwise).
  6. Continued synchronized motion beyond the original coordinate until the spindle actually stops and reverses.
  7. An unsynchronized move back to the original coordinate.
Spindle-synchronized motions wait for spindle index, so multiple passes line up. G33.1 moves end at the original coordinate.
G33.1 Example
G90 (set absolute mode)
G0 X1.000 Y1.000 Z0.100 (rapid move to starting position)
G33.1 Z-0.750 K0.05 (rigid tap a 20 TPI thread 0.750 deep)
M2 (end program)
It is an error if:
22. G38.x Straight Probe
G38.x axes
  • G38.2 - probe toward workpiece, stop on contact, signal error if failure
  • G38.3 - probe toward workpiece, stop on contact
  • G38.4 - probe away from workpiece, stop on loss of contact, signal error if failure
  • G38.5 - probe away from workpiece, stop on loss of contact
Important
You will not be able to use a probe move until your machine has been set up to provide a probe input signal. The probe input signal must be connected to motion.probe-input in a .hal file. G38.x uses motion.probe-input to determine when the probe has made (or lost) contact. TRUE for probe contact closed (touching), FALSE for probe contact open.
Program G38.x axes to perform a straight probe operation. The axis words are optional, except that at least one of them must be used. The axis words together define the destination point that the probe will move towards, starting from the current location. If the probe is not tripped before the destination is reached G38.2 and G38.4 will signal an error.
The tool in the spindle must be a probe or contact a probe switch.
In response to this command, the machine moves the controlled point (which should be at the center of the probe ball) in a straight line at the current feed rate toward the programmed point. In inverse time feed mode, the feed rate is such that the whole motion from the current point to the programmed point would take the specified time. The move stops (within machine acceleration limits) when the programmed point is reached, or when the requested change in the probe input takes place, whichever occurs first.
After successful probing, parameters 5061 to 5069 will be set to the coordinates of X, Y, Z, A, B, C, U, V, W of the location of the controlled point at the time the probe changed state. After unsuccessful probing, they are set to the coordinates of the programmed point. Parameter 5070 is set to 1 if the probe succeeded and 0 if the probe failed. If the probing operation failed, G38.2 and G38.4 will signal an error by posting an message on screen if the selected GUI supports that. And by halting program execution.
A comment of the form (PROBEOPEN filename.txt) will open filename.txt and store the 9-number coordinate consisting of XYZABCUVW of each successful straight probe in it. The file must be closed with (PROBECLOSE). For more information see the Comments Section.
An example file smartprobe.ngc is included (in the examples directory) to demonstrate using probe moves to log to a file the coordinates of a part. The program smartprobe.ngc could be used with ngcgui with minimal changes.
It is an error if:
  • the current point is the same as the programmed point.
  • no axis word is used
  • cutter radius compensation is enabled
  • the feed rate is zero
  • the probe is already in the target state
23. G40 Compensation Off
  • G40 - turn cutter radius compensation off. If tool compensation was on the next move must be a linear move and longer than the tool diameter. It is OK to turn compensation off when it is already off.
G40 Example
; current location is X1 after finishing cutter compensated move
G40 (turn compensation off)
G0 X1.6 (linear move longer than current cutter diameter)
M2 (end program)
See G0 & M2 sections for more information.
It is an error if:
  • A G2/G3 arc move is programmed next after a G40.
  • The linear move after turning compensation off is less than the tool diameter.
24. G41, G42 Tool Radius Compensation
G41 <D-> (left of programmed path)
G42 <D-> (right of programmed path)
  • D - tool number
The D word is optional; if there is no D word or if the D word is 0, the radius of the currently loaded tool will be used.
If supplied, the D word is the tool number to use. This would normally be the number of the tool in the spindle (in which case the D word is redundant and need not be supplied), but it may be any valid tool number.
To start tool radius compensation to the left of the part profile, use G41. G41 starts cutter radius compensation to the left of the programmed line as viewed from the positive end of the axis perpendicular to the plane.
To start tool radius compensation to the right of the part profile, use G42. G42 starts cutter radius compensation to the right of the programmed line as viewed from the positive end of the axis perpendicular to the plane.
The lead in move must be at least as long as the tool radius. The lead in move can be a rapid move.
Cutter radius compensation may be performed if the XY-plane or XZ-plane is active.
User M100-M199 commands are allowed when Cutter Compensation is on.
The behavior of the machining center when cutter radius compensation is on is described in the Radius Compensation Section along with code examples.
It is an error if:
  • The D number is not a valid tool number or 0.
  • The YZ plane is active.
  • Cutter radius compensation is commanded to turn on when it is already on.
25. G41.1, G42.1 Dynamic Cutter Radius Compensation
G41.1 D- <L-> (left of programmed path)
G42.1 D- <L-> (right of programmed path)
G41.1 & G42.1 function the same as G41 & G42 with the added scope of being able to program the tool diameter. The L word defaults to 0 if unspecified.
It is an error if:
  • The L number is not in the range from 0 to 9 inclusive.
  • The L number is used when the XZ plane is not active.
  • Cutter compensation is commanded to turn on when it is already on.
26. G43 Tool Length Offset
G43 <H->
  • H - tool number
  • G43 - use the currently loaded tool from the last Tn M6. G43 changes subsequent motions by offsetting the Z and/or X coordinates by the length of the tool. G43 does not cause any motion. The next time a compensated axis is moved, that axis’s endpoint is the compensated location.
  • G43 H- - use an offset from tool table. It is OK for the H number to be zero; the currently loaded tool will be used.
G43 H- Example Line
G43 H1 (set tool offsets using the values from tool 1 in the tool table)
It is an error if:
  • the H number is not an integer, is negative, or is not 0 or a valid tool number.
27. G43.1: Dynamic Tool Length Offset
G43.1 axes
  • G43.1 axes - change subsequent motions by offsetting the Z and/or X offsets stored in the tool table. G43.1 does not cause any motion. The next time a compensated axis is moved, that axis’s endpoint is the compensated location.
G43.1 Example
T1 M6 G43 (load tool 1 and tool length offsets, Z is at machine 0 and DRO shows Z1.500)
G43.1 Z0.250 (offset current tool offset by 0.250, DRO now shows Z1.250)
M2 (end program)
  • See G90 & T & M6 sections for more information.
It is an error if:
  • motion is commanded on the same line as G43.1
28. G49: Cancel Tool Length Compensation
  • G49 - cancels tool length compensation
It is OK to program using the same offset already in use. It is also OK to program using no tool length offset if none is currently being used.
29. G53 Move in Absolute Coordinates
G53 axes
To move in absolute coordinates from the machine origin, program G53 on the same line as a linear move. G53 is not modal and must be programmed on each line. G0 or G1 does not have to be programmed on the same line if one is currently active. For example G53 G0 X0 Y0 Z0 will move the axes to the home position even if the currently selected coordinate system has offsets in effect.
G53 Example Line
G53 G0 X0 Y0 Z0 (rapid linear move to the machine origin)
G53 X2 (rapid linear move to absolute coordinate X2)
  • See G0 section for more information.
It is an error if:
  • G53 is used without G0 or G1 being active,
  • or G53 is used while cutter radius compensation is on.
30. G54-G59.3 Select Coordinate System
  • G54 - select coordinate system 1
  • G55 - select coordinate system 2
  • G56 - select coordinate system 3
  • G57 - select coordinate system 4
  • G58 - select coordinate system 5
  • G59 - select coordinate system 6
  • G59.1 - select coordinate system 7
  • G59.2 - select coordinate system 8
  • G59.3 - select coordinate system 9
The coordinate systems store the axis values in the parameters shown in the following table.
Table 2. Coordinate System Parameters
Select CS X Y Z A B C U V W
G54
1
5221
5222
5223
5224
5225
5226
5227
5228
5229
G55
2
5241
5242
5243
5244
5245
5246
5247
5248
5249
G56
3
5261
5262
5263
5264
5265
5266
5267
5268
5269
G57
4
5281
5282
5283
5284
5285
5286
5287
5288
5289
G58
5
5301
5302
5303
5304
5305
5306
5307
5308
5309
G59
6
5321
5322
5323
5324
5325
5326
5327
5328
5329
G59.1
7
5341
5342
5343
5344
5345
5346
5347
5348
5349
G59.2
8
5361
5362
5363
5364
5365
5366
5367
5368
5369
G59.3
9
5381
5382
5383
5384
5385
5386
5387
5388
5389
It is an error if:
  • selecting a coordinate system is used while cutter radius compensation is on.
See the Coordinate System Section for an overview of coordinate systems.
31. G61, G61.1 Exact Path Mode
  • G61 - exact path mode. G61 visits the programmed point exactly, even though that means temporarily coming to a complete stop.
  • G61.1 - exact stop mode. Same as G61
32. G64 Path Blending
G64 <P- <Q->>
  • P - motion blending tolerance
  • Q - naive cam tolerance
  • G64 - best possible speed.
  • G64 P- <Q- > blending with tolerance.
  • G64 - without P means to keep the best speed possible, no matter how far away from the programmed point you end up.
  • G64 P- Q- - is a way to fine tune your system for best compromise between speed and accuracy. The P- tolerance means that the actual path will be no more than P- away from the programmed endpoint. The velocity will be reduced if needed to maintain the path. In addition, when you activate G64 P- Q- it turns on the naive cam detector; when there are a series of linear XYZ feed moves at the same feed rate that are less than Q- away from being collinear, they are collapsed into a single linear move. On G2/G3 moves in the G17 (XY) plane when the maximum deviation of an arc from a straight line is less than the G64 P- tolerance the arc is broken into two lines (from start of arc to midpoint, and from midpoint to end). those lines are then subject to the naive cam algorithm for lines. Thus, line-arc, arc-arc, and arc-line cases as well as line-line benefit from the naive cam detector. This improves contouring performance by simplifying the path. It is OK to program for the mode that is already active. See also the Path Control Mode Section and Trajectory Control Section for more information on these modes. If Q is not specified then it will have the same behavior as before and use the value of P-.
G64 P- Example Line
G64 P0.015 (set path following to be within 0.015 of the actual path)
It is a good idea to include a path control specification in the preamble of each G code file.
33. G90, G91 Distance Mode
  • G90 - absolute distance mode In absolute distance mode, axis numbers (X, Y, Z, A, B, C, U, V, W) usually represent positions in terms of the currently active coordinate system. Any exceptions to that rule are described explicitly in the G80 G89 Section.
  • G91 - incremental distance mode In incremental distance mode, axis numbers usually represent increments from the current coordinate.
G90 Example
G0 X2.5 (rapid linear move to coordinate X2.5 including any offsets in effect)
G91 Example
G91 (set incremental distance mode)
G0 X2.5 (rapid linear move 2.5 from current position along the X axis)
34. G90.1, G91.1 Arc Distance Mode
  • G90.1 - absolute distance mode for I, J & K offsets. When G90.1 is in effect I and J both must be specified with G2/3 for the XY plane or J and K for the XZ plane or it is an error.
  • G91.1 - incremental distance mode for I, J & K offsets. G91.1 Returns I, J & K to their default behavior.
35. G92 Coordinate System Offset
G92 axes
G92 makes the current point have the coordinates you want (without motion), where the axis words contain the axis numbers you want. All axis words are optional, except that at least one must be used. If an axis word is not used for a given axis, the coordinate on that axis of the current point is not changed.
When G92 is executed, the origins of all coordinate systems move. They move such that the value of the current controlled point, in the currently active coordinate system, becomes the specified value. All coordinate system’s origins are offset this same distance.
For example, suppose the current point is at X=4 and there is currently no G92 offset active. Then G92 x7 is programmed. This moves all origins -3 in X, which causes the current point to become X=7. This -3 is saved in parameter 5211.
Being in incremental distance mode has no effect on the action of G92.
G92 offsets may be already be in effect when the G92 is called. If this is the case, the offset is replaced with a new offset that makes the current point become the specified value.
It is an error if:
  • all axis words are omitted.
LinuxCNC stores the G92 offsets and reuses them on the next run of a program. To prevent this, one can program a G92.1 (to erase them), or program a G92.2 (to remove them - they are still stored).
See the Offsets Section for more information.
See the Parameters Section for more information.
36. G92.1, G92.2 Reset Coordinate System Offsets
  • G92.1 - reset axis offsets to zero and set parameters 5211 - 5219 to zero.
  • G92.2 - reset axis offsets to zero.
37. G92.3 Restore Axis Offsets
  • G92.3 - set the axis offset to the values saved in parameters 5211 to 5219
You can set axis offsets in one program and use the same offsets in another program. Program G92 in the first program. This will set parameters 5211 to 5219. Do not use G92.1 in the remainder of the first program. The parameter values will be saved when the first program exits and restored when the second one starts up. Use G92.3 near the beginning of the second program. That will restore the offsets saved in the first program.
38. G93, G94, G95: Feed Rate Mode
  • G93 - is Inverse Time Mode. In inverse time feed rate mode, an F word means the move should be completed in [one divided by the F number] minutes. For example, if the F number is 2.0, the move should be completed in half a minute.
    When the inverse time feed rate mode is active, an F word must appear on every line which has a G1, G2, or G3 motion, and an F word on a line that does not have G1, G2, or G3 is ignored. Being in inverse time feed rate mode does not affect G0 (rapid traverse) motions.
  • G94 - is Units per Minute Mode. In units per minute feed rate mode, an F word is interpreted to mean the controlled point should move at a certain number of inches per minute, millimeters per minute, or degrees per minute, depending upon what length units are being used and which axis or axes are moving.
  • G95 - is Units per Revolution Mode In units per revolution mode, an F word is interpreted to mean the controlled point should move a certain number of inches per revolution of the spindle, depending on what length units are being used and which axis or axes are moving. G95 is not suitable for threading, for threading use G33 or G76.
It is an error if:
  • Inverse time feed rate mode is active and a line with G1, G2, or G3 (explicitly or implicitly) does not have an F word.
  • A new feed rate is not specified after switching to G94 or G95
39. G96, G97 Spindle Control Mode
G96 <D-> S- (Constant Surface Speed)
G97 (RPM Mode)
  • D - maximum spindle RPM
  • S - surface speed
  • G96 D- S- - selects constant surface speed of S feet per minute (if G20 is in effect) or meters per minute (if G21 is in effect). D- is optional.
    When using G96, ensure that X0 in the current coordinate system (including offsets and tool lengths) is the center of rotation or LinuxCNC will not give the desired spindle speed. G96 is not affected by radius or diameter mode.
  • G97 selects RPM mode.
G96 Example Line
G96 D2500 S250 (set CSS with a max rpm of 2500 and a surface speed of 250)
It is an error if:
  • S is not specified with G96
  • A feed move is specified in G96 mode while the spindle is not turning
40. G73 Drilling Cycle with Chip Breaking
G73 X- Y- Z- R- Q- <L->
  • R - retract position along the Z axis.
  • Q - delta increment along the Z axis.
  • L - repeat
The G73 cycle is drilling or milling with chip breaking. This cycle takes a Q number which represents a delta increment along the Z axis.
  1. Preliminary motion.
    • If the current Z position is below the R position, the Z axis is traversed to the R position.
    • Move to the X Y coordinates
  2. Move the Z-axis only at the current feed rate downward by delta or to the Z position, whichever is less deep.
  3. Rapid up a bit.
  4. Repeat steps 2 and 3 until the Z position is reached at step 2.
  5. Retract the Z-axis at traverse rate to R.
It is an error if:
  • the Q number is negative or zero.
  • the R number is not specified
41. G76 Threading Cycle
G76 P- Z- I- J- R- K- Q- H- E- L-
images/g76-threads.png
Figure 3. G76 Threading
  • Drive Line - A line through the initial X position parallel to the Z.
  • P- - The thread pitch in distance per revolution.
  • Z- - The final position of threads. At the end of the cycle the tool will be at this Z position.
  • I- - The thread peak offset from the drive line. Negative I values are external threads, and positive I values are internal threads. Generally the material has been turned to this size before the G76 cycle.
  • J- - A positive value specifying the initial cut depth. The first threading cut will be J beyond the thread peak position.
  • K- - A positive value specifying the full thread depth. The final threading cut will be K beyond the thread peak position.
Optional settings
  • R- - The depth degression. R1.0 selects constant depth on successive threading passes. R2.0 selects constant area. Values between 1.0 and 2.0 select decreasing depth but increasing area. Values above 2.0 select decreasing area. Beware that unnecessarily high degression values will cause a large number of passes to be used. (degression = a descent by stages or steps.)
  • Q- - The compound slide angle is the angle (in degrees) describing to what extent successive passes should be offset along the drive line. This is used to cause one side of the tool to remove more material than the other. A positive Q value causes the leading edge of the tool to cut more heavily. Typical values are 29, 29.5 or 30.
  • H- - The number of spring passes. Spring passes are additional passes at full thread depth. If no additional passes are desired, program H0.
  • E- - Specifies the distance along the drive line used for the taper. The angle of the taper will be so the last pass tapers to the thread crest over the distance specified with E.' E0.2' will give a taper for the first/last 0.2 length units along the thread. For a 45 degree taper program E the same as K
  • L- - Specifies which ends of the thread get the taper. Program L0 for no taper (the default), L1 for entry taper, L2 for exit taper, or L3 for both entry and exit tapers. Entry tapers will pause at the drive line to synchronize with the index pulse then feed in to the beginning of the taper. No entry taper and the tool will rapid to the cut depth then synchronize and begin the cut.
The tool is moved to the initial X and Z positions prior to issuing the G76. The X position is the drive line and the Z position is the start of the threads.
The tool will pause briefly for synchronization before each threading pass, so a relief groove will be required at the entry unless the beginning of the thread is past the end of the material or an entry taper is used.
Unless using an exit taper, the exit move (traverse to original X) is not synchronized to the spindle speed. With a slow spindle, the exit move might take only a small fraction of a revolution. If the spindle speed is increased after several passes are complete, subsequent exit moves will require a larger portion of a revolution, resulting in a very heavy cut during the exit move. This can be avoided by providing a relief groove at the exit, or by not changing the spindle speed while threading.
The final position of the tool will be at the end of the drive line. A safe Z move will be needed with an internal thread to remove the tool from the hole.
It is an error if:
  • The active plane is not the ZX plane
  • Other axis words, such as X- or Y-, are specified
  • The R- degression value is less than 1.0.
  • All the required words are not specified
  • P-, J-, K- or H- is negative
  • E- is greater than half the drive line length
The sample program g76.ngc shows the use of the G76 canned cycle, and can be previewed and executed on any machine using the sim/lathe.ini configuration.
G76 Example
G0 Z-0.5 X0.2
G76 P0.05 Z-1 I-.075 J0.008 K0.045 Q29.5 L2 E0.045
In the figure the tool is in the final position after the G76 cycle is completed. You can see the entry path on the right from the Q29.5 and the exit path on the left from the L2 E0.045. The white lines are the cutting moves.
images/g76-01.png
Figure 4. G76 Example
42. Canned Cycles
The canned cycles G81 through G89 and the canned cycle stop G80 are described in this section.
All canned cycles are performed with respect to the currently-selected plane. Any of the six planes may be selected. Throughout this section, most of the descriptions assume the XY-plane has been selected. The behavior is analogous if another plane is selected, and the correct words must be used. For instance, in the G17.1 plane, the action of the canned cycle is along W, and the locations or increments are given with U and V. In this case substitute U,V,W for X,Y,Z in the instructions below.
Rotary axis words are not allowed in canned cycles. When the active plane is one of the XYZ family, the UVW axis words are not allowed. Likewise, when the active plane is one of the UVW family, the XYZ axis words are not allowed.
42.1. Common Words
All canned cycles use X, Y, Z, or U, V, W groups depending on the plane selected and R words. The R (usually meaning retract) position is along the axis perpendicular to the currently selected plane (Z-axis for XY-plane, etc.) Some canned cycles use additional arguments.
42.2. Sticky Words
For canned cycles, we will call a number sticky if, when the same cycle is used on several lines of code in a row, the number must be used the first time, but is optional on the rest of the lines. Sticky numbers keep their value on the rest of the lines if they are not explicitly programmed to be different. The R number is always sticky.
In incremental distance mode X, Y, and R numbers are treated as increments from the current position and Z as an increment from the Z-axis position before the move involving Z takes place. In absolute distance mode, the X, Y, R, and Z numbers are absolute positions in the current coordinate system.
42.3. Repeat Cycle
The L number is optional and represents the number of repeats. L=0 is not allowed. If the repeat feature is used, it is normally used in incremental distance mode, so that the same sequence of motions is repeated in several equally spaced places along a straight line. When L- is greater than 1 in incremental mode with the XY-plane selected, the X and Y positions are determined by adding the given X and Y numbers either to the current X and Y positions (on the first go-around) or to the X and Y positions at the end of the previous go-around (on the repetitions). Thus, if you program L10 , you will get 10 cycles. The first cycle will be distance X,Y from the original location. The R and Z positions do not change during the repeats. The L number is not sticky. In absolute distance mode, L>1 means do the same cycle in the same place several times, Omitting the L word is equivalent to specifying L=1.
42.4. Retract Mode
The height of the retract move at the end of each repeat (called clear Z in the descriptions below) is determined by the setting of the retract mode: either to the original Z position (if that is above the R position and the retract mode is G98, OLD_Z), or otherwise to the R position. See the G98 G99 Section.
42.5. Canned Cycle Errors
It is an error if:
  • axis words are all missing during a canned cycle,
  • axis words from different groups (XYZ) (UVW) are used together,
  • a P number is required and a negative P number is used,
  • an L number is used that does not evaluate to a positive integer,
  • rotary axis motion is used during a canned cycle,
  • inverse time feed rate is active during a canned cycle,
  • or cutter radius compensation is active during a canned cycle.
If the XY plane is active, the Z number is sticky, and it is an error if:
  • the Z number is missing and the same canned cycle was not already active,
  • or the R number is less than the Z number.
If other planes are active, the error conditions are analogous to the XY conditions above.
42.6. Preliminary and In-Between Motion
Preliminary motion is a set of motions that is common to all of the milling canned cycles. If the current Z position is below the R position, the Z axis is traversed to the R position. This happens only once, regardless of the value of L.
In addition, at the beginning of the first cycle and each repeat, the following one or two moves are made
  1. a straight traverse parallel to the XY-plane to the given XY-position,
  2. a straight traverse of the Z-axis only to the R position, if it is not already at the R position.
If another plane is active, the preliminary and in-between motions are analogous.
42.7. Why use a canned cycle?
There are at least two reasons for using canned cycles. The first is the economy of code. A single bore would take several lines of code to execute.
The G81 Example 1 demonstrates how a canned cycle could be used to produce 8 holes with ten lines of G code within the canned cycle mode. The program below will produce the same set of 8 holes using five lines for the canned cycle. It does not follow exactly the same path nor does it drill in the same order as the earlier example. But the program writing economy of a good canned cycle should be obvious.
Eight Holes
G90 G0 X0 Y0 Z0 (move coordinate home)
G1 F10 X0 G4 P0.1
G91 G81 X1 Y0 Z-1 R1 L4(canned drill cycle)
G90 G0 X0 Y1
Z0
G91 G81 X1 Y0 Z-0.5 R1 L4(canned drill cycle)
G80 (turn off canned cycle)
M2 (program end)
The G98 to the second line above means that the return move will be to the value of Z in the first line since it is higher that the R value specified.
images/eight.png
Twelve Holes in a Square
This example demonstrates the use of the L word to repeat a set of incremental drill cycles for successive blocks of code within the same G81 motion mode. Here we produce 12 holes using five lines of code in the canned motion mode.
G1 F50 X0 G4 P0.1
G91 G81 X1 Y0 Z-0.5 R1 L4 (canned drill cycle)
X0 Y1 R0 L3 (repeat)
X-1 Y0 L3 (repeat)
X0 Y-1 L2 (repeat)
G90 G0 X0 (rapid home)
Y0
Z0
M2 (program end)
images/twelve.png
The second reason to use a canned cycle is that they all produce preliminary moves and returns that you can anticipate and control regardless of the start point of the canned cycle.
43. G80 Cancel Canned Cycle
  • G80 - cancel canned cycle modal motion. G80 is part of modal group 0, so programming any other G code from modal group 0 will also cancel the canned cycle.
It is an error if:
  • Axis words are programmed when G80 is active.
G80 Example
G90 G81 X1 Y1 Z1.5 R2.8 (absolute distance canned cycle)
G80 (turn off canned cycle motion)
G0 X0 Y0 Z0 (turn on rapid traverse and move to coordinate home)
The following code produces the same final position and machine state as the previous code.
G0 Example
The advantage of the first set is that, the G80 line clearly turns off the G81 canned cycle. With the first set of blocks, the programmer must turn motion back on with G0, as is done in the next line, or any other motion mode G word.
If a canned cycle is not turned off with G80 or another motion word, the canned cycle will attempt to repeat itself using the next block of code that contains an X, Y, or Z word. The following file drills (G81) a set of eight holes as shown in the following caption.
G80 Example 1
N100 G90 G0 X0 Y0 Z0 (coordinate home)
N110 G1 X0 G4 P0.1
N120 G81 X1 Y0 Z0 R1 (canned drill cycle)
N130 X2
N140 X3
N150 X4
N160 Y1 Z0.5
N170 X3
N180 X2
N190 X1
N200 G80 (turn off canned cycle)
N210 G0 X0 (rapid home moves)
N220 Y0
N230 Z0
N240 M2 (program end)
Note
Notice the z position change after the first four holes. Also, this is one of the few places where line numbers have some value, being able to point a reader to a specific line of code.
images/G81mult.png
Figure 5. G80 Cycle
The use of G80 in line N200 is optional because the G0 on the next line will turn off the G81 cycle. But using the G80 as shown in Example 1, will provide for easier to read canned cycle. Without it, it is not so obvious that all of the blocks between N120 and N200 belong to the canned cycle.
44. G81 Drilling Cycle
G81 (X- Y- Z-) or (U- V- W-) R- L-
The G81 cycle is intended for drilling.
The cycle functions as follows:
  1. Preliminary motion to start position.
  2. Move the Z-axis only at the current feed rate to the Z position.
  3. Retract the Z-axis at traverse rate to clear Z. This cycle was used in the description of G80 above but is explained in detail here.
Example 1 - Absolute Position G81
Suppose the current position is (X1, Y2, Z3) and the following line of NC code is interpreted.
G90 G98 G81 X4 Y5 Z1.5 R2.8
This calls for absolute distance mode (G90) and OLD_Z retract mode (G98) and calls for the G81 drilling cycle to be performed once.
The X value and X position are 4.
The Y value and Y position are 5.
The Z value and Z position are 1.5.
The R value and clear Z are 2.8. OLD_Z is 3.
The following moves take place:
  1. a traverse parallel to the XY plane to (X4, Y5, Z3)
  2. a traverse parallel to the Z-axis to (X4, Y5, Z2.8).
  3. a feed parallel to the Z-axis to (X4, Y5, Z1.5)
  4. a traverse parallel to the Z-axis to (X4, Y5, Z3)
images/G81ex1.png
Example 2 - Relative Position G81
G91 G98 G81 X4 Y5 Z-0.6 R1.8 L3
This calls for incremental distance mode (G91) and OLD_Z retract mode (G98). It also calls for the G81 drilling cycle to be repeated three times. The X value is 4, the Y value is 5, the Z value is -0.6 and the R value is 1.8. The initial X position is 5 (=1+4), the initial Y position is 7 (=2+5), the clear Z position is 4.8 (=1.8+3), and the Z position is 4.2 (=4.8-0.6). OLD_Z is 3.
The first preliminary move is a traverse along the Z axis to (X1,Y2,Z4.8), since OLD_Z < clear Z.
The first repeat consists of 3 moves.
  1. a traverse parallel to the XY-plane to (X5, Y7, Z4.8)
  2. a feed parallel to the Z-axis to (X5, Y7, Z4.2)
  3. a traverse parallel to the Z-axis to (X5, Y7, Z4.8)
The second repeat consists of 3 moves. The X position is reset to 9 (=5+4) and the Y position to 12 (=7+5).
  1. a traverse parallel to the XY-plane to (X9, Y12, Z4.8)
  2. a feed parallel to the Z-axis to (X9, Y12, Z4.2)
  3. a traverse parallel to the Z-axis to (X9, Y12, Z4.8)
The third repeat consists of 3 moves. The X position is reset to 13 (=9+4) and the Y position to 17 (=12+5).
  1. a traverse parallel to the XY-plane to (X13, Y17, Z4.8)
  2. a feed parallel to the Z-axis to (X13, Y17, Z4.2)
  3. a traverse parallel to the Z-axis to (X13, Y17, Z4.8)
images/G81ex2.png
Example 3 - Relative Position G81
Now suppose that you execute the first G81 block of code but from (X0, Y0, Z0) rather than from (X1, Y2, Z3).
Since OLD_Z is below the R value, it adds nothing for the motion but since the initial value of Z is less than the value specified in R, there will be an initial Z move during the preliminary moves.
images/G81.png
Example 4 - Absolute G81 R > Z
This is a plot of the path of motion for the second g81 block of code.
Since this plot starts with (X0, Y0, Z0), the interpreter adds the initial Z0 and R1.8 and rapids to that location. After that initial Z move, the repeat feature works the same as it did in example 3 with the final Z depth being 0.6 below the R value.
images/G81a.png
Example 5 - Relative position R > Z
G90 G98 G81 X4 Y5 Z-0.6 R1.8
Since this plot starts with (X0, Y0, Z0), the interpreter adds the initial Z0 and R1.8 and rapids to that location as in Example 4. After that initial Z move, the rapid traverse move to X4 Y5 is done. Then the final Z depth being 0.6 below the R value. The repeat function would make the Z move in the same location again.
45. G82 Drilling Cycle, Dwell
G82 (X- Y- Z-) or (U- V- W-) R- L- P-
The G82 cycle is intended for drilling with a dwell at the bottom of the hole.
  1. Preliminary motion, as described above.
  3. Dwell for the P number of seconds.
  4. Retract the Z-axis at traverse rate to clear Z.
The motion of a G82 canned cycle looks just like G81 with the addition of a dwell at the bottom of the Z move. The length of the dwell is specified by a P- word in the G82 block.
46. G83 Peck Drilling Cycle
G83 (X- Y- Z-) or (U- V- W-) R- L- Q-
The G83 cycle (often called peck drilling) is intended for deep drilling or milling with chip breaking. The retracts in this cycle clear the hole of chips and cut off any long stringers (which are common when drilling in aluminum). This cycle takes a Q number which represents a delta increment along the Z-axis. The retract before final depth will always be to the retract plane even if G98 is in effect. The final retract will honor the G98/99 in effect. G83 functions the same as G81 with the addition of retracts during the drilling operation.
  3. Rapid back out to the retract plane specified by the R word.
  4. Rapid back down to the current hole bottom, backed off a bit.
  5. Repeat steps 2, 3, and 4 until the Z position is reached at step 2.
  6. Retract the Z-axis at traverse rate to clear Z.
It is an error if:
47. G84 Right-Hand Tapping Cycle
This code is currently unimplemented in LinuxCNC. It is accepted, but the behavior is undefined. See section G33.1
48. G85 Boring Cycle, Feed Out
G85 (X- Y- Z-) or (U- V- W-) R- L-
The G85 cycle is intended for boring or reaming, but could be used for drilling or milling.
  3. Retract the Z-axis at the current feed rate to clear Z.
49. G86 Boring Cycle, Spindle Stop, Rapid Out
G86 (X- Y- Z-) or (U- V- W-) R- L- P-
The G86 cycle is intended for boring. This cycle uses a P number for the number of seconds to dwell.
  4. Stop the spindle turning.
  5. Retract the Z-axis at traverse rate to clear Z.
  6. Restart the spindle in the direction it was going.
It is an error if:
  • the spindle is not turning before this cycle is executed.
50. G87 Back Boring Cycle
51. G88 Boring Cycle, Spindle Stop, Manual Out
52. G89 Boring Cycle, Dwell, Feed Out
G89 (X- Y- Z-) or (U- V- W-) R- L- P-
The G89 cycle is intended for boring. This cycle uses a P number, where P specifies the number of seconds to dwell.
  4. Retract the Z-axis at the current feed rate to clear Z.
53. G98, G99 Canned Cycle Return Level
  • G98 - retract to the position that axis was in just before this series of one or more contiguous canned cycles was started.
  • G99 - retract to the position specified by the R word of the canned cycle.
Program a G98 and the canned cycle will use the Z position prior to the canned cycle as the Z return position if it is higher than the R value specified in the cycle. If it is lower then the R value will be used. The R word has different meanings in absolute distance mode and incremental distance mode.
G98 Retract to Origin
G0 X1 Y2 Z3
G90 G98 G81 X4 Y5 Z-0.6 R1.8 F10
The initial (G98) plane is reset any time cycle motion mode is abandoned, whether explicitly (G80) or implicitly (any motion code that is not a cycle). Switching among cycle modes (say G81 to G83) does NOT reset the initial plane. It is possible to switch between G98 and G99 during a series of cycles.
